Bryan,
For RC input, mixed mode and linear control your DIP switch should read out 01 11 11. For exponential control it should be 01 11 01, which appears to be what you have set.
I would suggest commanding the motor controller with a different input mode, such as an analog pot to be sure that the motor controller itself is working properly. For that your DIP switch settings should be 11 11 01. Another option would be to use Dimension Engineering’s DEScribe software and a DELink. With this you can interface with the motor controller on your computer to see what’s going on and to configure it as needed.
As for general issues interfacing a spectrum with the Sabertooth motor controller, some creeping is possible but typically that can be resolved by trimming the controls on the remote and re-binding.
Regards,
Jason -